    Hi.
    I've just moved from Domoticz to MC, and so far I'm a happy chappy 🙂

    On domo I was controlling my heatpump/AC unit using Toni's setup, slightly altered to allow for my Panasonic inverter.
    I used his LUA script to calculate the needed codes to send to the AC.

    Now I'm trying to make the thing work on MC...

    I can send fixed commands, using the RAW feature, but I'm stuck trying to figure out a smart way of doing it on MC.

    Somehow I need to make the state of "Heatpump Mode (including ON/OFF)", "Fan Speed" and "Temperature Setting" work together to generate an eight digit code that will be send to the AC node when one of the parameters update.

    Any pointers (or solutions 😉 )

    Thanks 😄

    J 1 Reply Last reply 2 Jan 2017, 10:47 Reply Quote 0
    • J Offline
      jkandasa @ksga
      last edited by 2 Jan 2017, 10:47

      @ksga Thanks to showing interest with MyController. Can you post your program logic? We can create JavaScript and execute your logic 🙂

      K 1 Reply Last reply 4 Jan 2017, 16:15 Reply Quote 0
      • K Offline
        ksga
        last edited by ksga 1 Feb 2017, 18:00 2 Jan 2017, 12:29

        Sure @jkandasa
        The LUA script that Toni wrote looks like this:

        -- These are the configuration variables, set them according to your system
        modelCmd = '0'        -- Panasonic CKP, see https://github.com/mysensors/Arduino/blob/development/libraries/MySensors/examples/HeatpumpIRController/HeatpumpIRController.ino#L68
        textDev = 'IR data'   -- Name of the 'IR data' MySensors device
        irSendDev = 'IR send' -- Name of the 'IR send' MySensors device
        
        
        commandArray = {}
        
        
        for key, value in pairs(devicechanged) do
          if (key == 'Heatpump Mode' or key == 'Heatpump Fan Speed' or key == 'Heatpump Temperature') then
        
            mode = otherdevices['Heatpump Mode']
            fanSpeed = otherdevices['Heatpump Fan Speed']
            temperature = math.floor(otherdevices_svalues['Heatpump Temperature'])
        
            if     (mode == 'Off')   then powerModeCmd = '00'
            elseif (mode == 'Auto')  then powerModeCmd = '11'
            elseif (mode == 'Heat')  then powerModeCmd = '12'
            elseif (mode == 'Cool')  then powerModeCmd = '13'
            elseif (mode == 'Dry')   then powerModeCmd = '14'
            elseif (mode == 'Fan')   then powerModeCmd = '15'
            elseif (mode == 'Maint') then powerModeCmd = '16'
            end
        
            if     (fanSpeed == 'Auto')  then fanSpeedCmd = '0'
            elseif (fanSpeed == 'Fan 1') then fanSpeedCmd = '1'
            elseif (fanSpeed == 'Fan 2') then fanSpeedCmd = '2'
            elseif (fanSpeed == 'Fan 3') then fanSpeedCmd = '3'
            elseif (fanSpeed == 'Fan 4') then fanSpeedCmd = '4'
            elseif (fanSpeed == 'Fan 5') then fanSpeedCmd = '5'
            end
        
            temperatureCmd = string.format("%02x", temperature)
        
            modeCmd = '00' .. modelCmd .. powerModeCmd .. fanSpeedCmd .. temperatureCmd
        
            print(string.format('Mode: %s, fan: %s, temp: %s, modeCmd: %s', mode, fanSpeed, temperature, modeCmd))
        
            commandArray['UpdateDevice'] = otherdevices_idx[textDev] .. '|0|' .. modeCmd
            commandArray['IR send'] = 'On'
        
          end
        end
        
        return commandArray
        

        The code will generate an eight digit code looking something like this:
        12345678
        Position 1+2: Always "00", double zero
        Position 3: Model code - in my case "4" - refers to Arduino sketch
        Position 4+5: Power mode - for example "11" - Auto mode
        Position 6: Fan speed - for example "3" - speed 3
        Position 7+8: Temperature in hex - for example "18" - 24 degrees

        Above would result in the string: 00411318 - Auto mode, Fan speed 3, 24 degrees 🙂

        The mode, fanSpeed and temperature variables defined in the first section refers to the dummy devices that were needed on Domoticz

        1 Reply Last reply Reply Quote 0
        • K Offline
          ksga @jkandasa
          last edited by 4 Jan 2017, 16:15

          Hi @jkandasa
          I don't want to put any pressure on you or anything like that - I'm very grateful for all your hard work that has gone into this project - which ROCKS btw 🙂

          But - was my above info useful, or was it insufficient to explain the issue?

          J 1 Reply Last reply 5 Jan 2017, 07:41 Reply Quote 0
          • J Offline
            jkandasa @ksga
            last edited by jkandasa 1 May 2017, 18:34 5 Jan 2017, 07:41

            @ksga Sorry for the delay response,

            JavaScript code for the above LUA script,

            //Get sensor values with UID Tags
            var mode =  mcApi.uidTag().getByUid("hp-mode").getResource().getValue(); //Heatpump Mode
            var fanSpeed = mcApi.uidTag().getByUid("hp-fs").getResource().getValue(); //Heatpump Fan Speed
            var temperature = parseInt(mcApi.uidTag().getByUid("hp-temperature").getResource().getValue()).toFixed(0); //Heatpump Temperature
            
            var modelCmd = '0'; //Default
            var powerModeCmd = "00"; //Default value
            var fanSpeedCmd = "0"; //Default value
            
            //Update mode
            if (mode == 'off'){
              powerModeCmd = '00';
            }else if (mode == 'Auto'){
              powerModeCmd = '11';
            }else if (mode == 'Heat'){
              powerModeCmd = '12';
            }else if (mode == 'Cool'){
              powerModeCmd = '13';
            }else if (mode == 'Dry'){
              powerModeCmd = '14';
            }else if (mode == 'Fan'){
              powerModeCmd = '15';
            }else if (mode == 'Maint'){
              powerModeCmd = '16';
            }
            
            //Update Fan speed
            if (fanSpeed == 'Auto'){
              fanSpeedCmd = '0';
            }else if (fanSpeed == 'Fan 1'){
              fanSpeedCmd = '1';
            }else if (fanSpeed == 'Fan 2'){
              fanSpeedCmd = '2';
            }else if (fanSpeed == 'Fan 3'){
              fanSpeedCmd = '3';
            }else if (fanSpeed == 'Fan 4'){
              fanSpeedCmd = '4';
            }else if (fanSpeed == 'Fan 5'){
              fanSpeedCmd = '5';
            }
            
            var temperatureCmd = parseInt(temperature).toString(16).toUpperCase();
            if(temperatureCmd.length < 2) {
              temperatureCmd = '0' + temperatureCmd;
            }
            
            var modeCmd = '00'+modelCmd+powerModeCmd+fanSpeedCmd+temperatureCmd;
            
            // send to your IR
            // Get IR sensor via UID-Tag
            var irSensor = mcApi.uidTag().getByUid("my-ir-sen").getResource();
            // Update value
            irSensor.value = modeCmd;
            // Send value to sensor
            mcApi.sensor().sendPayload(irSensor);
            
            

            You have to set UID Tag for each sensor and get sensor value with UID Tag. There is no event mechanism in MC right now. You have to configure a timer job to run this operation.

            K 1 Reply Last reply 5 Jan 2017, 09:06 Reply Quote 0
            • K Offline
              ksga @jkandasa
              last edited by ksga 1 May 2017, 15:22 5 Jan 2017, 09:06

              No worries @jkandasa
              I'm trying to create the needed sensors. I assume I'll have to create some additional "dummy" sensors on the AC node.
              Is it possible to create a custom "Multi selector" sensor?
              The existing HVAC ones doesn't quite match the settings on my unit.

              Regarding the script itself - would it not need some logic to prevent it from sending the value if nothing has changed?
              I added the script on the "Utilities > Scripts tab" - created an "Execute Script" operation on the "Resources > Operations" tab, and finally a simple timer, running every 15 seconds, operating the "operation".

              If the script doesn't check for changes and stop if none has happened, I suspect that I will hear a most annoying beep from the heatpump four times every minute 🙂
              I won't mind, but I'm sure I will shortly be single again....

              UPDATE
              It works as I feared 😉
              Tried just doing "Text" sensors for holding the variables, and the code picks them up (except for fan speed), and sends them to the heatpump faithfully every time the script runs...
              Mildly annoying 😄

              Also, I think I should change from "simple" to "cron" for the timer. However it won't accept my cron entry "*/4 * * * * *" trying to make it run every 15 seconds...

              J 1 Reply Last reply 5 Jan 2017, 11:48 Reply Quote 0
              • J Offline
                jkandasa @ksga
                last edited by jkandasa 1 May 2017, 18:31 5 Jan 2017, 11:48

                @ksga

                Is it possible to create a custom "Multi selector" sensor?

                Right now it is impossible in MyController.

                Regarding the script itself - would it not need some logic to prevent it from sending the value if nothing has changed?

                you can check timestamp or previousValue of a sensor variable.

                timestamp >> would be a great one, you can make a condition with reference timestamp, if any one of sensorVariable timestamp changed, you can trigger further operation.
                previousValue >> compare value with previousValue, may not be a perfect solution! Might be changed multiple times within few seconds with the same value. Which leads false indication.

                I vote for timestamp solution, Here is simple check based on timestamp, For this you have to create new variable on Variable repository to take last execution time as a reference time. Create variable hp-lastcheck on Utilities >> Variables repository, add 0 as Value(default value, to avoid script null failure).

                //Get last check from variable repository
                var lastCheckVariable = mcApi.variable().get("hp-lastcheck");
                var lastCheck = lastCheckVariable.value;
                
                //Get sensor values with UID Tags
                var modeSensor =  mcApi.uidTag().getByUid("hp-mode").getResource(); //Heatpump Mode, sensor
                var fanSpeedSensor = mcApi.uidTag().getByUid("hp-fs").getResource(); //Heatpump Fan Speed, sensor
                var temperatureSensor = mcApi.uidTag().getByUid("hp-temperature").getResource(); //Heatpump Temperature, sensor
                
                // Take refrance of current time, to update last check
                var currentTime = Date.now();
                
                if(modeSensor.timestamp >= lastCheck || fanSpeedSensor.timestamp >= lastCheck || temperatureSensor.timestamp >= lastCheck){
                  // Update values
                  var mode =  modeSensor.getValue(); //Heatpump Mode
                  var fanSpeed = fanSpeedSensor.getValue(); //Heatpump Fan Speed
                  var temperature = parseInt(temperatureSensor.getValue()).toFixed(0); //Heatpump Temperature
                
                  var modelCmd = '0'; //Default
                  var powerModeCmd = "00"; //Default value
                  var fanSpeedCmd = "0"; //Default value
                
                  //Update mode
                  if (mode == 'off'){
                    powerModeCmd = '00';
                  }else if (mode == 'Auto'){
                    powerModeCmd = '11';
                  }else if (mode == 'Heat'){
                    powerModeCmd = '12';
                  }else if (mode == 'Cool'){
                    powerModeCmd = '13';
                  }else if (mode == 'Dry'){
                    powerModeCmd = '14';
                  }else if (mode == 'Fan'){
                    powerModeCmd = '15';
                  }else if (mode == 'Maint'){
                    powerModeCmd = '16';
                  }
                
                  //Update Fan speed
                  if (fanSpeed == 'Auto'){
                    fanSpeedCmd = '0';
                  }else if (fanSpeed == 'Fan 1'){
                    fanSpeedCmd = '1';
                  }else if (fanSpeed == 'Fan 2'){
                    fanSpeedCmd = '2';
                  }else if (fanSpeed == 'Fan 3'){
                    fanSpeedCmd = '3';
                  }else if (fanSpeed == 'Fan 4'){
                    fanSpeedCmd = '4';
                  }else if (fanSpeed == 'Fan 5'){
                    fanSpeedCmd = '5';
                  }
                
                  var temperatureCmd = parseInt(temperature).toString(16).toUpperCase();
                  if(temperatureCmd.length < 2) {
                    temperatureCmd = '0' + temperatureCmd;
                  }
                
                  var modeCmd = '00'+modelCmd+powerModeCmd+fanSpeedCmd+temperatureCmd;
                
                  // send to your IR
                  // Get IR sensor via UID-Tag
                  var irSensor = mcApi.uidTag().getByUid("my-ir-sen").getResource();
                  // Update value
                  irSensor.value = modeCmd;
                  // Send value to sensor
                  mcApi.sensor().sendPayload(irSensor);
                }
                
                //Update lastCheck refrence
                lastCheckVariable.value = currentTime;
                mcApi.variable().update(lastCheckVariable);
                

                I think I should change from "simple" to "cron" for the timer. However it won't accept my cron entry "*/4 * * * * *" trying to make it run every 15 seconds...

                In MyController cron is based on Quartz Scheduler. You should have at least one ? in your cron. Kindly refer this tutorial.
                For 15 seconds: 0/15 * * * * ?

                K 1 Reply Last reply 5 Jan 2017, 12:23 Reply Quote 0
                • K Offline
                  ksga @jkandasa
                  last edited by 5 Jan 2017, 12:23

                  @jkandasa
                  Thanks.. Will give it a go..

                  Is it also correct that the //Update Fan Speed should use
                  if (fanSpeed == 'Auto')

                  and not:
                  if (mode == 'Auto')
                  and so on...?

                  J 2 Replies Last reply 5 Jan 2017, 13:02 Reply Quote 0
                  • J Offline
                    jkandasa @ksga
                    last edited by 5 Jan 2017, 13:02

                    @ksga

                    Is it also correct that the
                    if (fanSpeed == 'Auto')
                    and not:
                    if (mode == 'Auto')
                    and so on...?

                    I am sorry it is a problem of copy/paste 😉 I have updated the script.

                    1 Reply Last reply Reply Quote 0
                    • J Offline
                      jkandasa @ksga
                      last edited by 9 Jan 2017, 18:15

                      @ksga Does this script works as you expected?

                      K 1 Reply Last reply 10 Jan 2017, 08:24 Reply Quote 0
                      • K Offline
                        ksga @jkandasa
                        last edited by 10 Jan 2017, 08:24

                        Hi @jkandasa
                        Sorry for not posting the feedback yet...

                        But yes - It works like a charm. And the timestamp solution seems to do what its supposed to 😄